Those plants need their CO2 though, so if the extraction fan is off for too long, they will be starving.
I worked through the numbers, but doesn't seem like you'd need much ventilation to provide the necessary CO2. From what I could google, most of plant water use is for transpiration and not photosynthesis. Humidity control may actually end up still governing your ventilation flow (and the associated heating needed for the incoming air).
Details are below for estimating CO2, and you can adjust them for your number of plants, etc. I haven't looked at ventilation needed for humidity control, though.
Estimating Air Flow for CO2 needs:
You can ballpark CO2 needed if you know your water consumption rate and the transpiration ratio for the plant species. The transpiration ratio is basically the ratio of water lost to transpiration (to move nutrients through the plant) vs. the water consumed in photosynthesis (i.e., combined with CO2).
I haven't found those ratios specific for cannabis, but they can be pretty high for some plant species - google says usually around 99% of water is transpired, only 1% is actually used in photosynthesis and combined with CO2.
(If anyone can find those ratios for cannabis, let me know.)
But, the equation basically works out to be:
(122 CFM of air) x (% water used for photosynthesis) x (L/day of total water that you use).
Let's say you have 6 plants using 1 L (each) every 3 days, and assume 10% goes to photosynthesis.
Then, they would be using 122 x (10%) x (1 / 3) x 6 = 24 cfm of total air, which isn't all that much.
Heating dry air is basically:
0.321 W per CFM per °F (difference between intake and exhaust air.
So, lets say 30 CFM, 30 °F outside air, 80 °F in tent:
0.321 x 30 x (80-30) = 481 W heating needed for the incoming air.